Max current setting

Started by EW Zuber, November 07, 2016, 04:55:15 PM

Previous topic - Next topic

EW Zuber

I'm wondering if the classic will limit the total current available when using more than one classic. In other words, if I set the master at 40A max bulk current will it also be able to limit all controllers to that 40A? I want to set up several array's in different directions but do not want the current to exceed a certain level while at the same time maximizing available current potential up to 40A.
(6) Solar World 175 watt, (14) Arco Solar 33 Watt, (15) REC 250 watt, 2KW Whirlwind turbine on 85' rohn 25 tower, Outback VFX 3648, Outback FM80 and Midnite Classic 150 w/WBJR, ( 8 ) Trojan L-16REB, 
WL7BDK

dgd

#1
Sorry, there is no communications between the Classics on current limiting. The follow-me logic forces same charge state between controllers and shares battery temperature so only one Classic needs a battery temp probe.
To do current limiting over several Classics you need an external processor to read and adjust current for each Classic in order to set an overall current limit for the battery bank
This not too difficult to do if you familiar with an rPi, arduino, BBB, etc..
Dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

Vic

#2
Eric,

There was a reference to battery charge current Limiting from Ryan in Reply #7 in this Thread:
http://kb1uas.com/mnsforum/index.php?topic=3133.msg29060#msg29060

Could not find the other Thread where you were alluding to this ...   hard to keep track.

Because different people call this function different things,  it is also difficult to Search the Forum to find all of the references to this.

The other comment on this function,  was that each Classic would need its WbJr and Shunt (IIRC).

GL,  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!