Voltage input limit for Classic 200?

Started by charlespyoung, December 31, 2016, 11:05:36 AM

Previous topic - Next topic

charlespyoung

I am considering upping the voltage from the array into the Classic 200 from 3 strings of 4 modules at 120V to 2 strings of 6 modules at 180V. Is that too much voltage? This is in Haiti so temps run from 70-90ºF.

Vic

Hi Charles,

Have you run your proposed configuration on the MidNite Classic String Sizer (?):
http://midnitesolar.com/sizingTool/displaySizing.php

Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

charlespyoung


Vic

OK,  Charles.   Did data from the String Sizer answer your questions?

Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

CDN-VT

I would also ask what is the battery voltage of the system ?
A huge step down will make the classic work harder .

Why is it you want to up the panel voltage ?
VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

charlespyoung

System battery voltage is 48V. We have 2 strings of 8 Rolls S-550's. That is why I posted this to the forum because I know I am in the upper limits of the CC and needing some additional input. I can go with 4 module PV circuits to be safer.

CDN-VT

Well that will be warm as with your Area for the classic to work 180 Vdc at  3 times the 60 Vdc the Cells need .
I would check the classic MNGP under temps & see what is NOW & after .. Voltage wise your good , but heat value is what would concern me.

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels