Tripping ground fault breaker

Started by PKsolar, January 27, 2017, 07:30:14 PM

Previous topic - Next topic

PKsolar

So everything has been running well since we found the fault in the LVD software. After a year of the charger running flawlessly, today I found the GF DC breaker tripped. This is the  MN GFP63 doubled .5A GF breaker in the MNDC 125 mini. I searched up and down and there are no loose wires, connections or frays. Could this be the Kid? Any suggestions? I'll test for stray voltage when the sun is out and a bit warmer tomorrow.

thanks for any input,
PK
10 Evergreen 215, 150 Classic, 48V (8x US Battery 400AH), MNPV Disco; Plus original system - 10 Evergreen, Fronius 2000 grid tie. 2014 added KID, Exeltech 1KW inverter, 12V (2 6V US Battery 400AH) to run garage. Classic 200 w 8 x 285 Solar World in Follow me mode.

ClassicCrazy

#1
Quote from: PKsolar on January 27, 2017, 07:30:14 PM
So everything has been running well since we found the fault in the LVD software. After a year of the charger running flawlessly, today I found the GF DC breaker tripped. This is the  MN GFP63 doubled .5A GF breaker in the MNDC 125 mini. I searched up and down and there are no loose wires, connections or frays. Could this be the Kid? Any suggestions? I'll test for stray voltage when the sun is out and a bit warmer tomorrow.

thanks for any input,
PK

Look for something that may have gotten moist or wet or bugs , webs, etc too.
Reset it and see if it happens again.
If you are not worried about code you don't really need that GFI breaker for your system - saying just in case it keeps tripping you can take it out of the circuit to see if controller works right and until you replace or don't replace it.