Absorb set to 55.2v. Classic goes from Bulk to absorb at 54.8v

Started by 5 Minutes 2 Midnite, July 11, 2017, 04:00:29 PM

Previous topic - Next topic

ClassicCrazy

Thanks Vic,
Yes now that you explain it I do remember reading about this in the past.
I guess it just takes a bigger load to drag the resting voltage down to let it get all sorted out .
Looking at it now hours later it is in Float and holding the system amps at zero but feeding the loads so it is all good.

I was watching it closer today since I had needed more power. Since the 48v lithium and 24v lead acid share the same combiner box with a split buss bar - I was able to take a string of the PV and switch it over from 24v to 48v system quite easily - all the strings are the same so no problems there. I just wired from bottom input of one breaker string to another breaker on the 48v buss bar. All I need to do is switch breaker to 24v off and breaker to 48v on . Simple !  here is my first attempt at using paint to make illustration
Larry



system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

Vic

Hi Larry,

That is a neat trick with the Combiner.

I will not mention what we do sometimes,  in switching things around in the Combiner,   HOT ...

Have fun,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

ClassicCrazy

Gotta make life interesting eh Vic ?

Well I did this hot - at least the one connection was - but I tried to be very careful.
The Midnite Din rail breakers do not clamp down on stranded 10 gauge very well - kept coming out - at least the type wire I was using - maybe more fine than course . I finally gave up and found a small piece of 8 or 6 gauge to use on it .

I have some of those insulated screwdrivers now too - so used those - makes it a little bit safer.

Larry