Through wire routing with 2 Classic charge controllers into 1 Epanel.

Started by Photowhit, September 04, 2012, 04:46:07 AM

Previous topic - Next topic

Photowhit

I had hoped to wire 2 Classic lites to 1 E-panel, mounted side by side. I think I've even seen an OK for this, but I want to have my array disconnects in the E-panel so I have quite a few wires going through a small conduit, so can I combine my chassis grounds? What about the PV / battery negative? Is this just a pass through so I could just connect them from one classic to the other?

If I run the network cable out to switch box, and wire an AC switch box, will a wireless network adapter inside my electrical cabinet be a code no no?

I guess I could finish reading through the manual... so perhaps the questions are answered, but 'ya all are great, hope I'm not too sleepy, but cool weather is coming and I can't sleep thinking about getting this project moving...
Home system 20 - 200watt Evergreen, E-Panel, 2-Classic Lite 150s up and running and 14 Suntech 185watt panels, and another Classic Lite in a dark room. Cabin system 8-115watt 12V, 6 - 170-5watt 24v, Pulse/Trace PC250 Power Center, 800AH 24V forklift Batt, ProSine 1800 watt (24v) inverter.