unusuaul "Resting"

Started by FredB, April 14, 2021, 05:04:21 PM

Previous topic - Next topic

FredB

I have a problem with one of my Classic 150 charge controllers going into "Resting" and staying there until the next day no matter how much I draw on the system.

System:
(3) Classic 150 charge controllers networked with "Follow Me" enabled.
WizBangJr installed.
(3) Simpliphi 48V 3.8 kWh batteries
(3) Arrays, one 1000 watt (Tracker), one 1750 watt (OldUsed), and one 2940 watt (BigArray) - this last one is the one I'm having trouble with.
All controllers have firmware version # 2193 network version # 2122

What I have done to try to resolve this;
I first noticed the BigArray controller was always "Resting" this was my oldest controller, I checked all connections did ohm and voltage checks and everything seemed OK so I updated the firmware, it worked for a couple of days and then went back to always Resting.  I thought it might be something wrong with the controller so I swapped it with my newest controller.  Upon boot up the new controller went immediately into Resting. (The old one works fine on the old array.) The next day it started working but it was the last to wake up. It's always the last. It goes thru the charge cycle and goes into Resting mode and no matter how much I draw on the system, it won't wake up.

I have tried a hard reset, and a soft reset, I have replaced the wiring from the combiner box to the controller, I have checked, and double checked, and tipple checked all connections, made sure everything is grounded, etc. The resting codes are normal i.e. 5 and 111. I'm pulling out my hair here, can anyone help?

I will try to upload pictures and the exported registers.



ClassicCrazy

#1
It is because your lithium batteries voltage is so high the Classic doesn't think it needs to be charged.
That is what the Reason for Resting seems to indicate.
When you put the loads on the system does the battery voltage drop ?
That is common for the controller to only do one charging cycle a day.
When it charges in the morning , is it replacing everything that has been taken out ?
Do you have SOC readings using Whizbang ?
Are the two controllers in Follow Me mode ?
It isn't uncommon for one charge controller to charge and the other to not when the batteries are high in voltage like that .
I see you have ending amps set to 0 - is that the following controller ? ( assuming you are using follow me and ending amps).

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

FredB

#2
Quote from: ClassicCrazy on April 14, 2021, 09:33:45 PM
It is because your lithium batteries voltage is so high the Classic doesn't think it needs to be charged.
That is what the Reason for Resting seems to indicate.

This is what I thought also at first but it didn't used to work this way. When I had loads on the system, it would either go into Float, Float MPPT, or MPPT as the other CC's do. I tried shutting the other controllers until about 50% SOC and it still won't come out of Resting.

When you put the loads on the system does the battery voltage drop ?

Yes, I ran it down as low as 51 VDC, (about 50% charged for these batteries) with the other CC's off and it still won't come out of Resting until the next day.

That is common for the controller to only do one charging cycle a day.
When it charges in the morning , is it replacing everything that has been taken out ?

Yes no problem there.

Do you have SOC readings using Whizbang ?

Yes but it's only accurate on the controller that's hooked to the Whizbang, the other CC's show 100% always. The Whizbang used to be hooked to the BigArray but I moved it to the OldArray thinking maybe it somehow could be the problem.

Are the two controllers in Follow Me mode ?

All three are yes.

It isn't uncommon for one charge controller to charge and the other to not when the batteries are high in voltage like that .
I see you have ending amps set to 0 - is that the following controller ? ( assuming you are using follow me and ending amps).

Ending amps are set to 4.5 but the system reaches Absorb set point for the 6 min. first.

Larry

Larry, the reason I started looking for a problem is, after working normally for several months after I upgraded to the Lithium batteries, the CC in question went into Resting for several days and nothing I did would bring it out. That's when I started with the firmware upgrade. Since the problem didn't move when I swapped controllers, I really don't think it's the controller but I just can't figure it out. Today I will just run the BigArray to see what happens.

jtdiesel65

Not to derail the thread, but what app are you using to see the data?
thx

FredB

I use both the Classic app on a Android device and the Local Status Panel on my Windows 7 PC. But don't use both at once! :)

UpNorthMan

Fred,
I don't have a classic so I'm shooting from the hip.
Is it possible that there is a voltage compensation value that is set to a wrong value and the second classic is resting because it can't send any power. Just a thought.

Wish you luck.
Ed
1000W panels Kid CC 230ah battery bank @48v
Weekend cabin, 250w inverter.
Waiting for the new inverter to be released so I can finish my install!

ClassicCrazy

Quote from: jtdiesel65 on April 15, 2021, 10:48:57 AM
Not to derail the thread, but what app are you using to see the data?
thx

That is the android Classic Monitoring app - available on Playstore.
or there are also some other versions that will work with MQTT.
https://github.com/ClassicDIY
more info also in the Homebrew Software section of the forums

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

ClassicCrazy

Quote from: FredB on April 15, 2021, 09:27:11 AM
Quote from: ClassicCrazy on April 14, 2021, 09:33:45 PM


Larry, the reason I started looking for a problem is, after working normally for several months after I upgraded to the Lithium batteries, the CC in question went into Resting for several days and nothing I did would bring it out. That's when I started with the firmware upgrade. Since the problem didn't move when I swapped controllers, I really don't think it's the controller but I just can't figure it out. Today I will just run the BigArray to see what happens.

Maybe this will give you some ideas ?
http://www.midniteftp.com/support/kb/faq.php?id=75

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

boB

#8
I was going to ask if one of your 2 or more Classics were running when the one Classic is resting.

Also, the battery temp sense can work over the Follow-Me.   Make sure both Classics are not set to master temp sense of course.


K7IQ 🌛  He/She/Me

FredB

#9
Yesterday I turned off the input to the 2 other Classics first thing in the morning, at the end of the charge cycle, the BigArray controller went into resting. The battery voltage dropped below the float set point and it stayed Resting. As I was flipping between the controllers in the Classic Monitoring app when I got to the BigArray, it flashed on the screen "No Power, waiting for power source" with full sun and 67 volts from the array! I tried shutting it down and back on - no change. I turned on the input to the other CC's and they immediately came up in MPPT Bulk. Watching the rest of the day, the BigArray always said "No Power, waiting for power source".

Larry, Interesting link. I might use the BTS as described in "Setting the mV/degC/cell to the lowest value without flipping the setting to DISABLE is about all we can do right now. This allows the BTS (Battery Temp Sensor) to function and this allows us to set an emergency HIGH BATTERY SHUTDOWN temperature in the LIMITS MENU under the CHARGE Menu in the Classic. When this temperature is sensed the Classic will stop charging to avoid a catastrophe."

All other settings are as per the newest Simpliphi Power integration guide"REV20201125".

boB, thanks, the BTS it disabled right now, but it is set correctly on the CC as master with the other 2 set to follow.

I am running out of ideas here. I did notice that the BigArray is at a slightly lower PV voltage than the other 2. BigArray 67V, Tracker 68V, and OldUsed 69V. I wonder if I was to rewire the BigArray to 100V if it would make a difference? Just grasping at straws.

ClassicCrazy

It seems you should use your digital volt meter and do some checking out your BigArray  for faults.
I would check all the wiring, connections, breakers, etc. Then if there was still and issue I would probably open circuit  voltage  and short circuit current test each PV module individually .
That would rule out problems with your PV array.
I think you said earlier that you had swapped around arrays to controllers and they all act the same with this BigArray ?
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

FredB

Quote from: ClassicCrazy on April 16, 2021, 11:57:09 AM
It seems you should use your digital volt meter and do some checking out your BigArray  for faults.
I would check all the wiring, connections, breakers, etc. Then if there was still and issue I would probably open circuit  voltage  and short circuit current test each PV module individually .
Larry
I like the way you think, I never thought about testing the panels! This morning I used my DC clamp meter to check each set of panels at the combiner box. I found one set that was about an amp lower than the rest and turned it off. I also set the 2 lower output controllers to .5V less (Absorb and Float) than the BigArray. Not sure which of these worked, but it's working correctly now. The BigArray is in float and the other 2 are resting. Code 38 "other charging sources appear to be active" This is as it should be. When I get more time I will figure out which it is and post the results here. Thanks for your help!

boB


Fred, what charge controller again ?

"No Power, waiting for power source"

I don't think we have a charger controller that says this.

Maybe that was the "app"  you are using.

So, did you have ONE charger controller with PV input and battery voltage BELOW the set point still not coming out of resting ?



boB
K7IQ 🌛  He/She/Me

FredB

Quote from: boB on April 16, 2021, 03:08:26 PM

Fred, what charge controller again ? "No Power, waiting for power source" I don't think we have a charger controller that says this. Maybe that was the "app"  you are using. So, did you have ONE charger controller with PV input and battery voltage BELOW the set point still not coming out of resting ?

boB
Yes it was the app saying "No Power, waiting for power source" and yes it was the CC I have named BigArray (on by itself) and it was not coming out of resting, but I think I can figure it out now. Please see my last post. Thanks for your help!

FNG

That is an awful low voltage for a 48v battery using MPPT, For example lets assume the lithium is at 52 you need 130% of that to wake up, So 67.6v. I am going to say the array voltage is just to low for MPPT charge controllers to work. I would suggest getting the voltage up closer to 100v