Wiring Classic with GFP enabled

Started by Westbranch, July 15, 2013, 07:36:39 PM

Previous topic - Next topic

Westbranch

I have been looking at a lot of wiring diagrams as well as the Classic Install Manual.

I think I just had and Ah Ha moment...

this diagram (for non integrated GFP) shows the ground from the CB as WHITE.
http://www.midnitesolar.com/pdfs/Charge_control_wiringGFP.pdf

Earlier I remember seeing in the Cl Manual that a white PV Neg connected, Fig 12  and 14 here:
http://www.midnitesolar.com/pdfs/classicManual.pdf

at the time I surmised that this was because of the connection to the common AC & DC grounding bus bar but now I am wondering as link 1 shows WHITE from the GFP to the Batt (-) buss...??

And on page 21
If the internal grounding jumper is installed in a Classic, the battery negative and DC source negative must not be connected to the system grounding conductor anywhere in the system

Can someone please explain this use of WHITE wire.  thanks

OR is this all mush brain thinking?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Halfcrazy

Yes the small breaker 0.5 or 1 amp is intended to physically bond DC negative to earth ground. This way if there is a Ground fault of sufficient amperage it trips that breaker and opens the paralleled breaker thus stopping the charging. So by nature one side of the breaker is green wire (Ground) the other is white wire (DC negative)

Ryan
Changing the way wind turbines operate one smoke filled box at a time

Westbranch

Sorry Ryan, I'm a bit slow getting it, but is this the correct interpretation of link 1,  WHEN using the built-in GFP?  (Link 1 shows the external 1 amp CB)

Use a white (PV Neg) wire to connect the Classic to the Battery /DC neg buss bar.
And the Neg grounding is done internally to/by the built-in GFP when a fault occurs.

I think I am getting system grounding and Lightning grounding confused, plodding through that scenario:

If an EMP occurs the SPD 300 will divert from PV (+) to ground, hopefully saving the install...

thanks

It truly hasn't sunk in yet but I think it is clearer...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Halfcrazy

Yes basically what the Classic does is this:

DC negative bus internally ---> 2 pin Jumper ---> 0.5 amp self healing fuse ----> Casting/Earth ground

So as you see there is a 0.5 Amp self healing fuse that (If the jumper is installed) bonds the DC negative bus to the Casting.

The rest of the earth ground system needs to be run as normal.

Ryan