MNPV3 Combiner + Classic 150/200 Charger, max. 100W Panels

Started by Tobit, November 15, 2013, 02:55:52 PM

Previous topic - Next topic

Tobit

I really like the 100W panels I've been using, they ship for free to my difficult access property unlike larger panels.

If I have a MNPV3 Combiner, how many 100W panels (specs listed below) can I go with if using a Classic 150 or 200W charge controller?  I am really having a hard time figuring out the math.  Thanks.

Optimum Operating Voltage (Vmp)   18.9V
Optimum Operating Current (Imp)   5.29A
Open - Circuit Voltage (Voc)   22.5V
Short- Circuit Current (Isc)   5.75A
Maximum Series Fuse Rating   15A

Westbranch

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

laszlo

Some more details about your system would be needed to do the calculations -- for example, what is your battery voltage, and the coldest recorded temperature in your location? Are you limited to only 3 PV combiner slots? 
4.6KW offgrid PV system, Classic 200, MX60, dual Magnum PAE 4448 inverters, Midnite combiner and disconnect boxes, e-panel,  WBJr, and 8 MN SPDs

Tobit

I will likely go with 24V battery bank.  Coldest temperature is around 0F.  I could go with a larger combiner but would rather not.

laszlo

With 24 Volts battery and Classic150,  you can series connect 5 of the above panels  in 3 strings with lots of comfort zone left both in terms of max amp (92A for 150) and max operating voltage (150Volts). You will need to use #4 wire from combiner to classic, and from classic to battery. It is possible to have 6 in series but IMO  it's not worth the stress and the unreliability it adds to the system. Code and best practices require overcurrent protection on the combiner output and the classic output -- so I would ause a Midnite mini-DC  with 4 breaker slots, or a Disco 6 slot,  so you can put a breaker for the output of the combiner in the same box.
4.6KW offgrid PV system, Classic 200, MX60, dual Magnum PAE 4448 inverters, Midnite combiner and disconnect boxes, e-panel,  WBJr, and 8 MN SPDs

Tobit

laszlo, thank you very much.  Ok, I think I will go with a 4x3 configuration.  It will produce much more than I need so I will have lots of fudge room.