lite not connecting

Started by GHOSTNH, August 04, 2014, 08:08:14 AM

Previous topic - Next topic

GHOSTNH

for the last 2 weeks the lite seems to be having issues connecting to the local app and mymidnite .  the only way i can get it back "on line" is to "cold boot" it ( remove the array and the battery)..  then it reconnects  and then i have to reset all the config parameters date time  voltage limits and the web settings ( yes i remember to save after ea setting) . i then have to use the bully menu to reboot it again so that the web  connection( mymidnite) will work.. this works ok for a day or two. then i am back to the same  not connect retrying issue for both the local app and mymidnite. . there have been no changes to the router or network.. seems this happens every 6 months or so ..

very frustrating  time consuming  and a pain in the butt to have to go thru every other day

if i leave the local app running 24/7 it seems to be ok??

suggestions ?
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen

atop8918

Hi,
Is the Lite in "Custom" Mode? If not then any configuration you do with the Local App will be lost after a reboot.

GHOSTNH

not in custom mode (i  need a set /known ip)...  if i do a cold boot ( no battery/no solar) YES all settings are lost .. which is why i do a BULLY menu reboo(t after setting the settings).  that keeps the settings  so mymidnite works
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen

GHOSTNH

firmware rev 1549
network 1547
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen

zoneblue

It does sound to me like your MNDP is not set to custom.  You MUST set it to custom in order to be able to use the local app to configure the lites. Otherwise evertime you reboot it the MNDP will reprogram the classic to the dip switch defaults, and youll lose local app settings.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

zoneblue

This is something that isnt totally clear from the instructions, but the reality is that MNDP custom is the only useful dipswitch setting. Youd only not use it if the classic was truly alone in the world, with no access to any other means of configuring it, and you didnt mind the inability to fine tune the settings.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

Halfcrazy

Also you "Should" be able to connect to it with the Local App and set a Static IP as well. So if you set the dip switches and get it running like you have. Log on to it with the Local app and verify everything. Then unplug the MNLP and set it to Custom and Plug it back in.

Now it will be a Static IP forever unless you change it with the Local App.

Also the new code Andrew released helps a lot with the Ethernet glitches so that may be worth a try as well

Ryan
Changing the way wind turbines operate one smoke filled box at a time

GHOSTNH

RYAN
did as suggested all settings set via app then  removed and unpluged MNLP. set s1 switches s1-s7 to custom (except no 8 eq still in man)


then repluged and replaced MNLP . we shall see what happens in the rest of the week
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen

GHOSTNH

new day same problem local app will not connect to controller.. CRAP!
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen

cybermaus

#9
Not sure if the lites have the same firmware generation as the non-lite classic. I have a non-lite myself

But for me the 1500 firmwares always had lots of connection problems. I gave up on the local app last year. Only when I upgraded to 1700's last winter (needed by WBjr SOC) did the connection from local app became mostly stable. It still looses connection every few weeks, but not often. Mind you, I do not have the last 17xx on there. Once SOC became stable, I am not so much bothered anymore, maybe the very last is even better on the connection.

Halfcrazy

GohstNH
Try rebooting the Classic without setting the dip switches and see if it comes back. i think it may be time to update the firmware to try and avoid these drop outs
Changing the way wind turbines operate one smoke filled box at a time

GHOSTNH

#11
Ryan
cold booted it and it did come back all  local app setting came back correct except the date.. no switchers were changed
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen

GHOSTNH

ryan has worked fine for 6+ months  with no changes with in my network.. now i believe in the last 6months  there has been some adobe air updates which have been installed
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen

Halfcrazy

Yeah I would try new firmware and see if that helps?
Changing the way wind turbines operate one smoke filled box at a time

GHOSTNH

ok so 3 hr later i have the firmware 1849 and network 1839 installed ( midnite sure needs to update it online firmware update instruction) a NEWBIE would never get it to work .. 

did the factory reboot (j1 j4)

local app connected  all  setting changed to previous setting  with except to the new local app menu items (i.e temp window battery status meter)  bully menu reboot

no s1 switch were changed (still in custom mode )

under info  i notice a db1-db5  with what appeasr to be hex values after them  not sure what that means ???

so we shall see what happens in the a.m.
12 Canadian solar 300 watt panels trace sw5548 two GNB battery banks 1200ahr and 1400ahr total 2600ahr 48v 1 classic lite  5kw backup gen