Wire size

Started by EW Zuber, August 11, 2014, 05:08:34 PM

Previous topic - Next topic

EW Zuber

It looks like the Classic 150 will take #4 wire to the mechanical terminals? Couldn't find this addressed in the manual.
(6) Solar World 175 watt, (14) Arco Solar 33 Watt, (15) REC 250 watt, 2KW Whirlwind turbine on 85' rohn 25 tower, Outback VFX 3648, Outback FM80 and Midnite Classic 150 w/WBJR, ( 8 ) Trojan L-16REB, 
WL7BDK

Vic

#1
Am (almost) certain that the Classic terminal block will accept #4 AWG Building Wire.  In the USA  cable like THHN should work-- 19 conductor type cable,  NOT Fine Stranded

It may be a bit of a tight fit into the block.

#4 AWG IS listed in the Breaker Sizing Table in the Classic Manual Appendix ...

Will try to look in Threads here,  as it has come up before.  FWIW,  73,    Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Westbranch

right below figure 17 on page 26 of the Classic owner’s manual


The Classic's DC terminal connectoris located on the circuit board as shown in. The connector will take up to a #4 AWG. #4 AWG THHN when installed in the Classic and MidNite E Panel is rated for over 100 amps and is therefore suitable for the highest power available from the Classic 150.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

...  AND on Pg 29 of the Jan '13 Classic Manual,   ...
"Maximum and Minimum Wire Size
The Classics Blue DC terminal connector will accept wire from #14-#4 AWG
The Classics Aux 1 and 2 terminal connector will accept wire up to #18 AWG   ... "

FWIW,  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Rybren

I THINK that the DIN rail breakers that many of us use will only accept up to #6 AWG
4 x 210W PV, Classic 150, e-panel, Samlex PST-1500-24, 232AH 24V

Vic

#5
You could use MNEDC Panel Mount breakers --  with ratings to 100 A.

AND,  these DIN-Rail breakers sized at 80 and 100 Amps,  accept up to # 2 AWG,  but occupy two DIN breaker spaces:

http://www.midnitesolar.com/productPhoto.php?product_ID=364&productCatName=Breakers&productCat_ID=16&sortOrder=19&act=p

http://www.solar-electric.com/installation-parts-and-equipment/midnite/cipr1/stfubr1/misomn150vdc.html

  FWIW.  Good Luck,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

vtmaps

Quote from: Vic on August 11, 2014, 05:21:04 PM
Will try to look in Threads here,  as it has come up before. 

Here's some early history of the Classic terminal block:
http://www.midniteforum.com/index.php?topic=581.0

Here's one from NAWS:
http://forum.solar-electric.com/showthread.php?16508

--vtMaps