Voltage output to diversion load

Started by asdex, September 07, 2014, 03:19:08 AM

Previous topic - Next topic

asdex

Hi, I wonder if someone can tell me if I have a Classic feeding a 24 volt battery bank for a PV array that can be up to a much higher voltage say 90 volts, when using the diversion feature what voltage will be supplied to the diversion load? Can the diversion load be supplied somehow from the Classic so that it is the same as battery voltage?
Thanks,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

dgd

The Classic does not feed a voltage (or power) to a diversion load. It will, however, provide an AUX signal that can be used to control a solid state relay that switches in the load to the battery.
This AUX signal could also be used to directly switch the load into the PV output.
There are many posts in this forum concerning both methods, some searching is the way to go...

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000