Classic stops output when large load applied and then recovers.

Started by Resthome, March 30, 2015, 09:45:55 PM

Previous topic - Next topic

Resthome

I am seeing what looks like a partial reset issue with the Classic 150 with the latest production firmware. This has happened twice now. Here is the sequence and a question for boB.

First the question for boB, what happens when the Classic is running as a 12v Solar and the battery voltage drops to 11.7 volts. What is the lowest operating voltage for the Classic to maintain it’s charging function?

Now the issue...

1.   Classic is in Float at 13.5v. Sun is late in afternoon.
2.   A 150 A load is applied from an Inverter when a microwave is turned on.
3.   ReBulk is set to 11.5v the Classic Charge Stage goes from 6 to 0 and the Classic output current goes to 0 and the daily kWh resets to 0
4.   At 14 sec the Classic is still at 0 output current but the WBjr begins too show the -150v load.
5.   At 24 sec the Classic is still at 0 output current but goes from charge stage 0 to 4.
6.   At 28 sec the Classic begins to show output current of 66.9A and the Battery voltage goes to 12.7 V
7.   The 150A load from the Inverter was on for a total of 2 minutes or slightly less.
8.   The Classic is now charging the batteries but the daily kWh have been reset and other daily parameters like float time may have also reset.

I’ll attach the data from the Local App as soon as I can. Is this just a case of the initial hit dropping the voltage too low for the Classic to function? Doesn't seem like it is as it stays with that load for 2 minutes and the Classic starts applying output around 28 sec.

Added Local App Live Data Output.

I know I should have grabbed the RFR number but I didn't. If I have to I will try to duplicated it when I return.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

kitestrings

Any chance you're seeing an "OCP error" when, or just after this occurs (and/or a red screen on the local app)?

Resthome

Quote from: kitestrings on March 30, 2015, 10:44:01 PM
Any chance you're seeing an "OCP error" when, or just after this occurs (and/or a red screen on the local app)?

Did not see either.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Resthome

Quote from: Resthome on March 30, 2015, 09:45:55 PM
I am seeing what looks like a partial reset issue with the Classic 150 with the latest production firmware. This has happened twice now. Here is the sequence and a question for boB.

First the question for boB, what happens when the Classic is running as a 12v Solar and the battery voltage drops to 11.7 volts. What is the lowest operating voltage for the Classic to maintain it’s charging function?

Now the issue...

1.   Classic is in Float at 13.5v. Sun is late in afternoon.
2.   A 150 A load is applied from an Inverter when a microwave is turned on.
3.   ReBulk is set to 11.5v the Classic Charge Stage goes from 6 to 0 and the Classic output current goes to 0 and the daily kWh resets to 0
4.   At 14 sec the Classic is still at 0 output current but the WBjr begins too show the -150v load.
5.   At 24 sec the Classic is still at 0 output current but goes from charge stage 0 to 4.
6.   At 28 sec the Classic begins to show output current of 66.9A and the Battery voltage goes to 12.7 V
7.   The 150A load from the Inverter was on for a total of 2 minutes or slightly less.
8.   The Classic is now charging the batteries but the daily kWh have been reset and other daily parameters like float time may have also reset.

I’ll attach the data from the Local App as soon as I can. Is this just a case of the initial hit dropping the voltage too low for the Classic to function? Doesn't seem like it is as it stays with that load for 2 minutes and the Classic starts applying output around 28 sec.

Added Local App Live Data Output.

I know I should have grabbed the RFR number but I didn't. If I have to I will try to duplicated it when I return.
Any comments from boB or Ryan on this?
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

boB

RH, I don't suppose you could re-create that and video the MNGP screen ?

>>>.   ReBulk is set to 11.5v the Classic Charge Stage goes from 6 to 0 and
the Classic output current goes to 0 and the daily kWh resets to 0 <<<

Sounds kind of like that load is dropping the voltage to the Classic's battery side and is making it reset ?
That is one reason for it to reset its kW-Hour reading of course.

The Classic's auxiliary power supply should operate down to around 6 volts or so.  Maybe you could
try wiring the Classic's positive wire (at least the + wire) more directly to the battery positive
terminal just in case that large surge load is pulling too much current through the Classic wiring.

We have seen OCP's happen because of this and it ~could~ also cause the Classic's input
voltage to drop significantly.  Kind of like a car's starter motor drops the voltage.

The RFR number would show if the Classic reset or not as well.  But you say that the
WB Jr. was working ?  Maybe that was from the Local App ?  If so, you may need to look
at the MNGP display or video it if you can re-create this problem.

>>> 6.   At 28 sec the Classic begins to show output current of 66.9A and the Battery voltage goes to 12.7 V <<<

Went to 12.7 V but from what low V  ?  I don't suppose you were able to catch the lowest battery
voltage during this 2 minute time ?  And does that 150 amp surge start out higher than 150 amps or
just 150 A ?

Re-Bulk won't cause the Classic to stop charging.  An OCP could but that wouldn't reset the kW-Hours.

I think that if the Classic does a reset, the Local App will not necessarily show you that but it would
disconnect from the Classic I would think and that in itself might be a giveaway.
boB
K7IQ 🌛  He/She/Me

Resthome

Quote from: boB on April 01, 2015, 07:46:34 PM
RH, I don't suppose you could re-create that and video the MNGP screen ?

>>>.   ReBulk is set to 11.5v the Classic Charge Stage goes from 6 to 0 and
the Classic output current goes to 0 and the daily kWh resets to 0 <<<

Sounds kind of like that load is dropping the voltage to the Classic's battery side and is making it reset ?
That is one reason for it to reset its kW-Hour reading of course.

The Classic's auxiliary power supply should operate down to around 6 volts or so.  Maybe you could
try wiring the Classic's positive wire (at least the + wire) more directly to the battery positive
terminal just in case that large surge load is pulling too much current through the Classic wiring.

We have seen OCP's happen because of this and it ~could~ also cause the Classic's input
voltage to drop significantly.  Kind of like a car's starter motor drops the voltage.

The RFR number would show if the Classic reset or not as well.  But you say that the
WB Jr. was working ?  Maybe that was from the Local App ?  If so, you may need to look
at the MNGP display or video it if you can re-create this problem.

>>> 6.   At 28 sec the Classic begins to show output current of 66.9A and the Battery voltage goes to 12.7 V <<<

Went to 12.7 V but from what low V  ?  I don't suppose you were able to catch the lowest battery
voltage during this 2 minute time ?  And does that 150 amp surge start out higher than 150 amps or
just 150 A ?

Re-Bulk won't cause the Classic to stop charging.  An OCP could but that wouldn't reset the kW-Hours.

I think that if the Classic does a reset, the Local App will not necessarily show you that but it would
disconnect from the Classic I would think and that in itself might be a giveaway.
boB

boB ... 

I only noticed this after reviewing the Local App data that was recorded during this period. I do not believe the voltage went any lower that what is shown. In the data I provide in the Excel sheet. The inverter never kicked off and it would have at about 11.3 V.  It was a microwave turning  on under inverter power so I don't believe there was a surge above the 150A. The lowest voltage is shown as 11.7 V before the Classic recovered and the voltage went back up. See data.

The Classic is wired directly to the battery as is the inventer. So don't believe that the current was being pulled through the Classic wiring. I don't see any gap in the time stamps ( every 2 sec) of the locL app data if there was a reset I would thing the local app disconnect during this period would show in the time stamps.

We are back home so would have to try to record this after we return in a couple of weeks. Just what screen on the MNGP a do you want to see? 
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

boB


I would settle to see the MNGP screen when that load comes on.  If you weren't watching
the MNGP, then you may not have noticed if there was an OCP either.
I don't think that the Local App shows this ?  It certainly doesn't log it.

Yeah, the voltage most likely does not drop all too far, otherwise your microwave oven
would not keep running.

Looking for data, now.
THanks
boB
K7IQ 🌛  He/She/Me

boB


I see from your data that this is a VERY strange problem that I have no idea of what is
going on. Looks like the Classic did not reset...  I can't see that it did anyway.  I REALLY
wish that this would log the RFR # along with all the other good data.

Will look into this.  Very strange.
Will look to see what version of firmware you are using as well.  I hope that is in here.

A video of the MNGP main screen might help IF you can get it to do this again.


BUT !!!  If it did NOT reset, then WHY does the WB Jr. amps go to zero when your\
microwave oven was drawing  150 amps ???

Here is that little interval where something screwed up.

-13.3
-13.3
-13.3
-13.3
-13.3
0
0
0
0
-60
-60
-149.7
-149.7
-145.1
-145.1

I think the question I have is, what was the Classic doing in that little interval ?
The Local App was definitely reading battery voltage because I see the change
from   11.9  ... 11.8 .....   11.7 volts during that 0 amp interval.

You got a good one here !

You can probably just ignore my last posting.

boB
K7IQ 🌛  He/She/Me

Resthome

boB

It's the latest production firmware. It did the same thing two days in a row. The thing that made me notice it was the daily kWh look low. So it went through the logs looking at the kWh a saw it higher that what the daily total was showing that is where I saw it go to zero, along with the current and then I saw the 150A load come back in and realized that was when I started the microwave because it will pull a little under 150A.  Since I had started the microwave the day before when the Classic was in Float I when look at that set of logs and saw exactly the same thing.

Other than this the Classic has seemed to be performing okay at least the limited daily data seems okay. There was one day in February that the daily data was missing though, not sure what that was about, it just did not show that day's data in the log at all. The next day the data was back. Although this is only our second trip up this year where we stayed for a few days to really monitor it with the local app.

I may have seen this a year ago as there was one day that the Classic was showing no current out and I checked the PV array breakes and all was fine and I could not figure out what was going on. I think I reverted to reseting the Classic in that case, but I'm pretty sure the microwave was involved can't be positive but I remember my wife heating her coffee back up. Was only their for one day so don't think I have LA data from then but will go back and look.

Any additional data I can provide let me know. Thanks again for looking at this.

John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

boB


OK, so while I am looking through code, next time you go to the boat, rack up at least 0.1 kW-Hour and
then start up the microwave to heat some water or something. for maybe 30 seconds.
See if you can repeat that.  If it resets when you do this, do it again and see if it resets the kW-Hours again.

Hopefully you can be watching the MNGP when your wife or whoever turns on the microwave also.

150 (or so) amps /10 is about right for a microwave.  15 amps AC or so ?

Thanks,
boB
K7IQ 🌛  He/She/Me

Resthome

John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Halfcrazy

How big is the battery in AH?
Is it sealed or flooded?
How old is it?

I am wondering if there is a momentary dip north of say 8v on the classics terminals?

Ryan
Changing the way wind turbines operate one smoke filled box at a time

kitestrings

"north", or "south"?  Maybe it is relative to which hemisphere you're in ;)

Resthome

Quote from: Halfcrazy on April 02, 2015, 09:45:18 AM
How big is the battery in AH?
Is it sealed or flooded?
How old is it?

I am wondering if there is a momentary dip north of say 8v on the classics terminals?

Ryan

840Ah 6x2V cell for 2V Flooded - Solar One - New Oct 2012

The Invertor would have kicked off if the voltage went below 11.3V and that did not happen as the microwave continued to run for the full 2 minutes. That voltage drop would have to be quicker than the 2sec voltage interval on the LA data. The lowest voltage recorded was 11.7V by the Classic and the LA. it appears from the LA data that the Classic went from Float, to Float MPPT, Resting, then Bulk MPPT. The question is why RESTING and why did the kWh reset to 0 for the day?? Note in the data I provide in post above there is NO gap in the time sequence. I'm open to all suggestions.

The next time we are up I can attach my Fluke MM and have it record lowest and highest voltage at the Classic terminal during this test.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Resthome

Quote from: kitestrings on April 02, 2015, 10:56:26 AM
"north", or "south"?  Maybe it is relative to which hemisphere you're in ;)
Classic have been know to do strange things. But I doubt if it cares where it is at.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA