Charge rate for batteries

Started by asdex, November 17, 2015, 05:22:43 PM

Previous topic - Next topic

asdex

Hi, just wanted to check that I'm calculating this right. My battery specs say bulk charge is 7.35 volts per six volt battery. I have two sets of four batteries in series then paralleled together for 24 volts. Would I set the bulk charge rate in the Classic at 29.4 volts? absorb at 29.4 volts and float at 26.4 volts?
I have just got these specs as our batteries are branded differently so haven't checked the Classic yet for time of absorb but I think I remember seeing this in the menu.
Thanks,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

Westbranch

you only need to set the Absorb and Float voltages, the Classic takes care of the rest.  A good starting point is 2 hrs for Absorb, if they don't perform to spec then increase the time...

hth
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

#2
Hi asdex.

Most Solar chargers do not have a setting for Bulk voltage (this is customarily seen on On-Grid battery chargers),  so you do not need to worry about a Bulk voltage setting.

29.4 volts should be fine for your Absorption voltage,  as this IS equal to 7.35 V per 6 V battery.   Be certain to set the Temperature Compensation value in the Classic's Temp Comp page in the Charge menu  -- it appears that your batteries need a setting of about --3 mV per cell.

AND,  the Absorption time required by batteries is directly dependent upon the Depth Of Discharge DOD) experienced in the previous discharge cycle.  Two hours may not be a bad place to start.  You can set the Absorb time in the Charge menu,  in the Time page.

Measuring the Specific Gravity of each cell with your Hydrometer is the best measure of how well your charge parameters are working to charge your battery bank on a given day.

The battery data notes that the Target SG for fully charged batteries is 1.270.

Vic