Aux 1 configuration

Started by asdex, November 18, 2015, 10:28:53 PM

Previous topic - Next topic

asdex

Just wanted to check, it says on the side of my Classic  “Aux Output 1- 13 vdc 200mA, reconfigurable as 3.3 vdc aux output.”
I thought it could be a clean contact as well. I have it working as a clean contact driving a 24 volt DC relay but are concerned that this is correct or not.
In the manual it says: “Aux 1 Function OUTPUT = Relay or 12V/0V Signal jumper selectable” so the sticker on the outside of my Classic doesn’t seem to line up.
Thanks,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

Halfcrazy

Yes the label is backwards:

Aux1- 500ma dry contact or 13v/200ma output
Aux2- 13v/200ma out or configurable as 3.3vdc input
Changing the way wind turbines operate one smoke filled box at a time

asdex

6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

Halfcrazy

That was a good find, that sticker has been wrong since day one 6 years ago and no one noticed  :o