Temp sensor

Started by Priusron, May 06, 2016, 02:47:37 AM

Previous topic - Next topic

Priusron

I have installed LiFrP04 batteries. Everything I read says to not use temp compensation. Can I leave the temp sensor hooked up to monitor the temps and just turn off temp compensation in the menus?

RossW

Manual says:

Quote
Battery Temperature Compensation

The Classic comes with a battery temperature sensor (BTS). This sensor raises or lowers charge voltage
based on temperature. Connect BTS to the BATT TEMP jack
The Battery temperature menu appears as T-Comp in the BATTERY MENU. In this menu
you can change the voltage compensation as needed

Presumably it doesn't have any practical min/max limits, so setting it to 0mV/degC would be "off"
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

zoneblue

While i havent tried it, but i recall bob saying that it wouldnt go to zero, but that you could use 0.1

6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

CDN-VT

i do 0
my cells are in in earth , constant temp , cool .
Im building a much larger one now , since there is NO maintenance of cooling
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.