Isolating battery bank from Classic

Started by asdex, July 20, 2016, 03:49:11 PM

Previous topic - Next topic

asdex

Hi, I noticed this comment while reading questions and answers on the forum:
"the classic wont like having the battery removed with the pv still connected. If you do this you'll need to remove the pv first."

So is it correct that is isn't good to isolate the batteries from the Classic while the PV panels are still connected?
If so what problems will it cause? I have a circuit breaker between my battery bank and the Classic.
Thanks,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

Resthome

Quote from: asdex on July 20, 2016, 03:49:11 PM
Hi, I noticed this comment while reading questions and answers on the forum:
"the classic wont like having the battery removed with the pv still connected. If you do this you'll need to remove the pv first."

So is it correct that is isn't good to isolate the batteries from the Classic while the PV panels are still connected?
If so what problems will it cause? I have a circuit breaker between my battery bank and the Classic.
Thanks,

You should also have a Breaker on the PV at the controller so the PV can be disconnected from the controller.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

asdex

Yes, I have that as well. But should I always turn off the PV first?
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

Vic

#3
Quote from: asdex on July 20, 2016, 03:49:11 PM

    "So is it correct that is isn't good to isolate the batteries from the Classic while the PV panels are still connected?
If so what problems will it cause? I have a circuit breaker between my battery bank and the Classic.
Thanks   ..."

Hi asdex,

As noted by Resthome,  it is good practice to always shut OFF the PV input breaker to the CC first,  then open the battery breaker.  AND  when re-powering the CC,  do the reverse  --  battery breaker ON first,  PV input breaker second.

The result in not doing things the proper way are essentially unpredictable.   You might get away doing things backward,  but  the results may result in  improper behavior of the CC.

The battery voltage operates the CC,   not the PV input,  at least for most MPPT CCs.

Also,  it is a very good idea to place both the PV in,  and battery breakers for the CC close to the CC,  within arm's-reach.

The above is good practice for any CC
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

asdex

Thanks for that. Yes I have them close (as per picture attached.
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

Vic

asdex,

Thanks for the pic,  nice clean installation,  using some creativity.

Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

boB

Well, I suppose the answer depends on what you are planning on doing with
the  Classic's battery terminals  while it is still running off of
only the PV input.  I disconnect the battery from the Classic quite a bit
without any problems.

If you turn off the battery and the Classic stays running and then reconnect
that same battery a moment later, it should also be OK.

If you were planning on reconnecting a DC load like an inverter to the Classic's battery terminals
with the battery disconnected, then there would be very little filtering on the
battery side and if the load is very large, the 120 Hz ripple current might not be so good
for the Classic's battery side capacitors...  But usually, in say, Solar tracking mode,
turning off the battery breaker will just make the Classic shut off from the PV input
because it sees a large-ish change in power and thinks it's time to sweep.

boB
K7IQ 🌛  He/She/Me

asdex

Thanks for your replies. I'll make sure I isolate the PV panels first from now on. Its generally when I have wanted to work on the batteries I haven't taken note of which one I turn off first. I will now.
Cheers,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North. 2x 24volt 280ah LiFePO4 batteries in parallel, Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Victron BMV-712 monitor, Alibaba solar pump.

boB


Yes, just working on the system, it doesn't matter which one you turn off first.

PV first I suppose but shouldn't really matter.

boB