Started by kauaisolarman, October 10, 2016, 05:17:28 AM

Previous topic - Next topic

dgd

Quote from: CDN-VT on October 12, 2016, 12:26:18 AM
I can't see how have 2 different solar arrays on 2 separate controllers & the 2 different arrays are faced in different directions will work well in Follow me ,

I agree. I can't figure out what advantage Follow-me gives in this situation.
I would also have connected both arrays to one Classic.

Dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

kauaisolarman

Quote from: dgd on October 12, 2016, 04:26:18 PM
Quote from: CDN-VT on October 12, 2016, 12:26:18 AM
I can't see how have 2 different solar arrays on 2 separate controllers & the 2 different arrays are faced in different directions will work well in Follow me ,

I agree. I can't figure out what advantage Follow-me gives in this situation.
I would also have connected both arrays to one Classic.

Dgd

even is 1 string has Vmp of 73 and the other Vmp115.2?

should i just parallel these 2 strings together?

2 solar systems in progress;
1. 24V interstate battery; 5x sanyo hit 190Watt in parallel to classic 150-SL + 8x Shell 140 watt series/parallel to classic 150-Sl (follow me).

2. 48V aquion battery; 6x panasonic HIT 325, 6x suniva 315,  CC TBD.

dgd

Quote from: kauaisolarman on October 12, 2016, 08:16:46 PM

even is 1 string has Vmp of 73 and the other Vmp115.2?

should i just parallel these 2 strings together?

only if the Vmp is near same on both strings, you hadn't said before  they were different or did I miss that info?
Have you considered a sig/info with your profile that details what equipment/PVs etc you are using. That basic info would make answering questions a lot easier and relevant.
I would still have considered trying to use just one Classic and reconfiguring the PVs to get closer Vmps

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

CDN-VT

even is 1 string has Vmp of 73 and the other Vmp115.2?

should i just parallel these 2 strings together?


NO do not Parallel them , you have two classics ?
Use them both & post your panel harvest sizing .
Set the later harvest classic to what the batterys top charging s are so it will take over & let the first morning classic start , is how I would do it . say .5 of a volt lower & check with DVM while working & adjust in tweaks to read main batterys correct . SAme as afternoons setup.

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels