ground fault protection question

Started by kauaisolarman, October 11, 2016, 04:48:18 AM

Previous topic - Next topic

kauaisolarman

hello

I have purchased midnite solar GFP circuit breaker for my midnite KID as prescribed in the wiring diagrams by the KID manuals.

do i also need to use these Midnite GFP circuit breakers with the Classic and Classic-SL models also? 

or are they not needed because the Classics and Classic-SL both have built in GFP?

just want to make sure i'm not missing a GFP circuit breaker between the PV and CC (like the KiD needs).

thanks
2 solar systems in progress;
1. 24V interstate battery; 5x sanyo hit 190Watt in parallel to classic 150-SL + 8x Shell 140 watt series/parallel to classic 150-Sl (follow me).

2. 48V aquion battery; 6x panasonic HIT 325, 6x suniva 315,  CC TBD.

Halfcrazy

They would not be needed on the classics as all classic models have ground fault built in
Changing the way wind turbines operate one smoke filled box at a time