Classic won't start

Started by krementz, October 24, 2017, 02:42:11 PM

Previous topic - Next topic

krementz

My neighbor's off-grid solar system stopped working, and she is away for the winter.

She has a 24V system (4 6V Rolls in series). Voltage is now about 10 volts. Yeah, pretty bad. She had left the inverter on. One of the PV circuit breakers in the combiner box had tripped. Her "smart" charger  (from generator) won't charge the batteries.

The Classic is non-responsive - nothing on the screen. My assumption is the voltage from the batteries is just too low to fire up the Classic. Can the Classic start on just solar power, with no working batteries?

I tried turning off the panels, hold down both arrow keys, and turning on the PV again. Nada.

I will try to charge each half of the batteries with a small 12 volt dumb charger so maybe I can get system voltage up to 22V or so, which I think would then restart the Classic. There is no portable 24V charger on the island. What is the minimum voltage for the Classic to run?

Or is it likely the Classic is fried or something?

She just got the Rolls, so it is worth the effort to try and resuscitate them. I realize they may be damaged, but I hope not fatally.

Any other ideas or suggestions?



Way off grid
Old system: Outback 2524, 1200 W PV,  installed 2005, 384 amp hours
New System: 2 SMA 6048 with 2 Midnite Solar Classic 150 controllers, 5500 W PV, 1700 amp hours

ClassicCrazy

#1
Best thing to try is what you said - see if you can get charge into batteries enough so  that they have enough voltage to turn on the Classic - it won't turn on if battery voltage is too low . 
If the batteries have sulfated up so much that they will not come up in voltage then there isn't much you can do - the batteries are bad.
If you caught them soon enough and get some charge in them then there should be hope .

I just wonder what made the PV breaker trip - maybe another problem ?
Be interesting to know how much load is on the system that took it down so low . Not sure what kind of inverter but seems like it should have shut off when voltage got too low to save the batteries - most do .
You said just one of the PV tripped - if there are multiple strings of PV in a combiner box the others should have done some charging . Or did the main PV breaker trip ?

Whatever - sounds like some investigation with a digital volt meter and checking the whole system for connections is in order.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

CDN-VT

If you have the clearance to do the work !
I would check the system out , Disconnect the inverter & the batterys into a 12Volt setup 2x2  , use the charger & get it up to 12 volts , Fire up the classic with a reboot & pick 12Vdc to help the charger . After a time , Back to 24Vdc battery & then Reboot the Classic to see 24Vdc . Right now it's all about saving the batterys .

VT 
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

dgd

Krementz,

Connect the solar panels directly to battery bank. If you have sufficient sun then a few days should get the bank voltage up for you to reconnect the Classic and see if the batteries have come good.

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

KyleM

The Classic only needs about 10.5 to 11 volts to come on. FYI

Once he Classic comes on it only needs about 32 volts coming off the PV in order to start BULK charging since this is a 24 volt system.   (24x130%=31.6)

Before you go tearing up the system I would just try and get the Classic to boot up by using an alternative method to get the batteries over 11 volts.
Kyle M

krementz

I "bumpstarted" the batteries by dividing into 2x12, with a tiny 6A dumb charger and a 20A smart charger hooked in parallel.

That was enough to get the Classic running again. It was also enough to let the inverter charger charge from the generator.

Rainy today, so essentially no PV today, but it looks like all is well. Won't know the final condition of the batteries for quite a while; l hope we get some sunshine soon.
Way off grid
Old system: Outback 2524, 1200 W PV,  installed 2005, 384 amp hours
New System: 2 SMA 6048 with 2 Midnite Solar Classic 150 controllers, 5500 W PV, 1700 amp hours

Westbranch

don't forget to check for a hot battery (6V) on the ones(?) that were not still holding a charge.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

bee88man

So, what caused the breaker to trip?

CDN-VT

Assuming here

Back feed into the panels ??

VT

Glad I see 2x2  & getting better ,
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

krementz

I don't know what would cause a breaker from the PV panels to the combiner to trip. No lightning happened. No grid to backfeed. Generator has been off.

There is a MS blue light surge protector. With the tripped breaker off, it lights as normal. If the bad circuit is held in place, it goes out.

My first thought was some chafed insulation on the roof, but further reflection tells me that that would not make sense. Superficial inspection of the roof panels look OK.

Anybody have any ideas? I don't know what I am looking for.
Way off grid
Old system: Outback 2524, 1200 W PV,  installed 2005, 384 amp hours
New System: 2 SMA 6048 with 2 Midnite Solar Classic 150 controllers, 5500 W PV, 1700 amp hours

ClassicCrazy

#10
If the Surge Protector blue LED is on when the circuit is open but goes off when the circuit is closed and energized that says something is pretty goofy.  I am assuming you are talking about the DC circuit .  Is this surge protector on the combiner box outside , or inside at the main DC panel ?
Maybe you can draw out a schematic or take a photo inside of the box where the surge protector is connected -- not sure how deep you digging into this system or your skills .
Someone needs to evaluate the system for troubles.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

CDN-VT

#11
Also if your system was a 24Vdc with an inverter & you swapped the battery connections to make a 12Vdc (2x2) the inverter should NOT be part of the system in a mode of 12Vdc !!
So how is the gen charger through the inverter working ?

Quote from: krementz on October 25, 2017, 02:03:57 PM
It was also enough to let the inverter charger charge from the generator.

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

krementz

The combiner box with the blue surge protector is inside on PV DC side, between the panels and the Classic. The Classic then goes to a combiner box with the inverter cables, and cables to the batteries.

I separated the batteries to two 12V pairs, with the inverter disconnected. The little dumb charger was enough to activate the smart charger. so I could charge each pair with 26A until it about 11.5V. Same with the other pair. Removed the portable chargers, reconnected the pair, then ran her crappy 15A 24V charger off the generator. I calculate it will take 20-30 hours to recharge if the inverter really is a continuous 15A, which I doubt. It is not a 3-stage charger.

With about 15 hours run time, the batteries rest about 25.5V, so making progress.


Way off grid
Old system: Outback 2524, 1200 W PV,  installed 2005, 384 amp hours
New System: 2 SMA 6048 with 2 Midnite Solar Classic 150 controllers, 5500 W PV, 1700 amp hours

CDN-VT

Very Good to hear !
Well done

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

Vic

krementz,

If it is possible to fully-charge the batteries,   and measure the SG of each cell,   as a reference (record these SGs),   and EQ the bank,   this would be a good idea.

It is common for Flooded batteries that have been discharged to this low level,   to have some cells that were discharged to zero volts,   and then,  further discharge tries to charge those cells in REVERSE polarity.   If this is the case,   usually those cells/batteries may appear to be more,  or less fully-charged,   until they need to supply loads (without a CC or charger supplying power).  Since  those cells really have little Capacity to supply loads for any real amount of time,   the battery bank voltage often crashes.

Another sign of this,  is that the apparent self-discharge rate seems high,   and these cells/batteries usually have lower terminal when rested over night,   even with no external load on the battery bank.

Hope that the above is not the case.

Good Luck,   Vic