Not getting Full SG using my Conext SW charger

Started by Matrix, January 13, 2018, 03:05:10 PM

Previous topic - Next topic

Matrix

Your thoughts and help will be appreciated: 

I am having a hard time getting my SW 4024 to finish a charge for my Trojan L16 435 amp hour batteries (x4 in series) .  I get to an SG of 1.266-76 (depending on the cell) and the Classic says I am at 99% SOC with only 433 amp hours.  Trojan says 100% is 1.277 and when I did an EQ last week,  I noted the SG in all cells stopped rising between 1.286 and 1.295 according to my Hydro,  so I took the average of those hi numbers and have tried to use  that as a target for 100% charged (because my hydro may be off).

I have raised the Absorb timer to max so it is not timing out ... and have raised the Absorb voltage to 31.2 and temp comp to -5 (so today they were charging at 31.5 +/-).  That is getting near EQ voltage.   :o


I Found this thread
and read most of it ....  I noticed the OP has an Schneider Conext SW Inverter/Charger.   So I asked there too.

But I am wondering,  the Schneider Conext SW 4024 does not have an end amp setting like the Classic.  BUT it does ask for the Battery Bank Capacity in Amp Hours.  I cannot see a reason why the SW would need to "know" the amp hours (it does not report SOC) except to set End Amps.  I did kinda confirm that is the case noting that the charge seemed to kick to float from absorb at about 8.7 amps which equals 435 ah x 2%.    So I tried setting the AH in the SW to 100 and it ended at about 4.5 amps.  But the batteries were already about 99% charged. 

What is the best way to get my SG to rise on up to my Base Line of about 1.288 (on my hydro) that I establish using an EQ until the SG stopped rising?  Should I continue to raise the Absorb Volts?  The SW also has bulk volt setting.  Should that be the same as the Absorb setting?  I set it lower so I do not over gas the batteries. 

Thoughts?  Thanks.

Mike
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

ClassicCrazy

I guess I am not following you .
So you are using the equalize SG to base your 100% full SG on instead of the manufacturer recommened SG which is lower ?

An equalize charge is an overcharge . Doing that continually is not good for the lifespan of the batteries.

What are the SOC settings you have in the Classic ?  Those are probably what is keeping it from showing 100% . You can change the efficiency setting on that if you need to get it to read 100% .  The SOC is just an estimate gauge not a real perfect gauge.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Vic

#2
Mike,

YES,  Schneider CCs and many of their inverters use a FIXED 2% of the battery Capacity that has been entered  as the EA value  --  Schneider programmers (the humans)  seem to be a very non-creative lot.  SO,   anything that they can force the user do calculate and enter into their hardware,   they do  gleefully,  with a chuckle.

So one is forced to lie to their hardware about the Capacity of the battery,   to change the value of this dim-witted EA function (IMO).

IIRC,   you are using a Hydrovolt (?).   Which should be temperature compensated for its readings.   If so,  it might be possible that it could take a bit of time for the  compensated to show up.

Had asked before,   if you have been using the procedure for measuring SG  that had been Linked  --  Surrette's  Measuring Specific Gravities.  Believe that Trojan has a similar one ...   the method one uses to take SGs   DOES   matter.   Have you read either of these,   and are you doing as suggested?

Do you RINSE,   Rinse,   and RINSE  again after EACH SG measuring session ??

Also,  some variation in SGs,  cell-to-cell,   can be attributed to some variation in battery temperatures,   and in electrolyte levels,   but,  neither of these should be very large factors.

With a very good Hydro,  about the best repeatability  is 5 points,   and that does not include  Calibration  error.

Also, it is often recommended that one measures SGs while the battery is being Floated,  several hours after the end of an Absorption or EQ charge.

Your batteries  should have stabilized now,   as they probably have more than about 75-ish cycles.

One other thing,  is,  if you have significant Opportunity Loads on your system,  when approaching your EA setting,  even small voltage drops in connecting cables (and even breakers),  can have a relatively large effect on the duration of Absorb,  when using EA.   This is the result of a voltage drop in cables/breakers lowering the charge voltage at the battery terminals, compared to what the CC believes is the voltage,   thus reducing battery charge current in Absorb,   and causing early Absorb termination (for CCs without battery voltage Sense terminals/leads).

Just a drive-by,  FWIW,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Matrix

Quote from: ClassicCrazy on January 13, 2018, 05:20:14 PM
I guess I am not following you .
So you are using the equalize SG to base your 100% full SG on instead of the manufacturer recommened SG which is lower ?

An equalize charge is an overcharge . Doing that continually is not good for the lifespan of the batteries.


Larry,  You are more or less correct.  But this is what I am being told on another forum.  Set a baseline and charge to that. 

I am understanding that 100% SG is the number at which SG stops rising.  If this is not true, Are you saying that SG can go higher than 100%?  That is,  if my Hydro is accurate,  and the manufacture says full  is 1.277 ... then any number over that is over charged,  and that it is possible to have higher SG numbers than 100%? 

I was watching carefully the number at which SG stopped rising and using that number (for the past few days) thinking perhaps my Hydrovolt is off and low. 

As of yet,  in 3 months i have not had to add any water to the batteries.  Even with 4-5 EQ charge sessions.

Quote from: ClassicCrazy on January 13, 2018, 05:20:14 PM
What are the SOC settings you have in the Classic ?  Those are probably what is keeping it from showing 100% . You can change the efficiency setting on that if you need to get it to read 100% .  The SOC is just an estimate gauge not a real perfect gauge.

Larry

Where are the SOC settings?  Is that the battery efficiency setting in the Local App?   Battery Efficiency is set to 94%

Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

#4
Quote from: Vic on January 13, 2018, 06:58:35 PM
Mike,

YES,  Schneider CCs and many of their inverters use a FIXED 2% of the battery Capacity that has been entered  as the EA value  --  Schneider programmers (the humans)  seem to be a very non-creative lot.  SO,   anything that they can force the user do calculate and enter into their hardware,   they do  gleefully,  with a chuckle.

So one is forced to lie to their hardware about the Capacity of the battery,   to change the value of this dim-witted EA function (IMO).


Yes ... that is what I have found.  I am not impress with Schneider,  find that the SW does not work as advertised,  and if I could do it all again,  I would run far far away from Schneider products.  (But I bet the B17-3  is going to be over my pay grade  :-\ ... but it looks cool)

So am I correct.  The best way to control End Amps in the SW would be to change the Battery Capacity function?

Quote from: Vic on January 13, 2018, 06:58:35 PM
IIRC,   you are using a Hydrovolt (?).   Which should be temperature compensated for its readings.   If so,  it might be possible that it could take a bit of time for the  compensated to show up.

Had asked before,   if you have been using the procedure for measuring SG  that had been Linked  --  Surrette's  Measuring Specific Gravities.  Believe that Trojan has a similar one ...   the method one uses to take SGs   DOES   matter.   Have you read either of these,   and are you doing as suggested?

Do you RINSE,   Rinse,   and RINSE  again after EACH SG measuring session ??
Yes to all


Quote from: Vic on January 13, 2018, 06:58:35 PM
Also,  some variation in SGs,  cell-to-cell,   can be attributed to some variation in battery temperatures,   and in electrolyte levels,   but,  neither of these should be very large factors.

With a very good Hydro,  about the best repeatability  is 5 points,   and that does not include  Calibration  error.

Also, it is often recommended that one measures SGs while the battery is being Floated,  several hours after the end of an Absorption or EQ charge.
The 2nd Hydrovolt I received seems to be very accurate at least to itself.  It seems to get repeatbable numbers in the same cell after the 3 draws from each cell.    It is consistently 7 points higher than my glass Hydro,  which is why I am targeting 1.285 instead of 1.277.  But you are right.  I do need to wait a bit after EQ to take a final reading. 


Quote from: Vic on January 13, 2018, 06:58:35 PM
Your batteries  should have stabilized now,   as they probably have more than about 75-ish cycles.

One other thing,  is,  if you have significant Opportunity Loads on your system,  when approaching your EA setting,  even small voltage drops in connecting cables (and even breakers),  can have a relatively large effect on the duration of Absorb,  when using EA.   This is the result of a voltage drop in cables/breakers lowering the charge voltage at the battery terminals, compared to what the CC believes is the voltage,   thus reducing battery charge current in Absorb,   and causing early Absorb termination (for CCs without battery voltage Sense terminals/leads).

Just a drive-by,  FWIW,   Vic

Thanks. 

Again,  my main question was charging with the SW and if I should continue to raise the absorb volts ... or if lowering the Battery capacity would cause a longer End Amp charge.  Seems the lower capacity "Cheat" might be the better way to go.    Using an absorb of 31.3v today ... the SW kicked off into float while the batteries where at 1.265 on the Hydrovolt.    Even if the Hydro is accurate to a T,  that is still too low. 
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

boB


The way I understand it, EA shouldn't be used ALL the time...  i.e.  you will need to do a timed absorb (2 or 3 or 4 hours ?) once per week or
so.  This is to desulfate the plates and get the sulfuric acid back in solution.  The more it sticks to the plates, the lower the SG will be able to get.

If the batteries are not disharged, then the Ending Amps will stop the charge without having to go the 2 or 3 hours to do a good
anti-sulfation.  This is what the skip-days feature is supposed to do.  But I think it can work better with the EA and be a bit smarter.

The battery can be recharged back to 100% by putting back the amp-hours taken out plus the AH inefficiency (extra 5% to 10% usually)

Absorbing or EQing for a "long enough" time should ensure that the battery has gotten a FULL @^# charge (Anti-Sulfation-Stage)

Then, the State Of Charge should assume to be 100% of whatever the capacity actually is.  Might be better, might be worse than the
label rating of the battery.

This is how I understand it anyway.

boB
K7IQ 🌛  He/She/Me

ClassicCrazy

#6
Quote from: Matrix on January 13, 2018, 09:34:55 PM
Quote from: ClassicCrazy on January 13, 2018, 05:20:14 PM
I guess I am not following you .
So you are using the equalize SG to base your 100% full SG on instead of the manufacturer recommened SG which is lower ?

An equalize charge is an overcharge . Doing that continually is not good for the lifespan of the batteries.


Larry,  You are more or less correct.  But this is what I am being told on another forum.  Set a baseline and charge to that. 

I am understanding that 100% SG is the number at which SG stops rising.  If this is not true, Are you saying that SG can go higher than 100%?  That is,  if my Hydro is accurate,  and the manufacture says full  is 1.277 ... then any number over that is over charged,  and that it is possible to have higher SG numbers than 100%? 

I was watching carefully the number at which SG stopped rising and using that number (for the past few days) thinking perhaps my Hydrovolt is off and low. 

As of yet,  in 3 months i have not had to add any water to the batteries.  Even with 4-5 EQ charge sessions.

Quote from: ClassicCrazy on January 13, 2018, 05:20:14 PM
What are the SOC settings you have in the Classic ?  Those are probably what is keeping it from showing 100% . You can change the efficiency setting on that if you need to get it to read 100% .  The SOC is just an estimate gauge not a real perfect gauge.

Larry


Where are the SOC settings?  Is that the battery efficiency setting in the Local App?   Battery Efficiency is set to 94%

I think I remember a battery dealer telling me that some battery manufacturers run the SG hot ( too high ) to get increased claims of battery capacity at the expense of battery longevity .  Not sure if I have that exactly correct but the point was that it wasn't good to run the SG too high . If you look at specs many manufacturers give a range of absorb voltages and this would correlate to the SG going higher if it is over charged. The way I see it is with new batteries to run the bottom of the range and then raise it as needed over the years to compensate for aging of the batteries or other factors.

hey my memory was correct ! just found this "  Some manufacturers use specific gravities as high as 1.320 in an attempt to gain additional Ah capacity, but at the cost of a shorter cycle life. "  also nice interpretive graph of what Bob was mentioning about SG changes http://giantbatteryco.com/GLOSSARY/Specific.Gravity-Industrial.Batteries.html


Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Matrix

So there is a hi number I Could go to ... but shouldn't necessarily go that hi ?  Correct?  Better to stay closer to the Manufacture printed 100% full SG regardless of it the SG can go higher?   OK 

So what if I am getting say an average of 1.285 from the 3 cells in on battey,  But the other 3 batteries and 9 cells are all closer to 1.270.  Do I charge until the lowest cell of the 12 hits 1.277? (that is going to put my highest cell up to about 1.292) ...OR... do I average the cells and shut for that number in the highest cell? 

Right now today,  we have had full sun all day in NE Florida.  I was down to 79% and charging stared at about 9am and went thru to 1:15pm when absorb stopped with a about 3,500 Watts going back into the battery bank.   So I am seeing it got a good charge.    SG on my known lowest cell was 1.278 and on the known highest cell was 1.292.   Did I charge too long?
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

Quote from: boB on January 13, 2018, 11:49:56 PM

The way I understand it, EA shouldn't be used ALL the time...  i.e.  you will need to do a timed absorb (2 or 3 or 4 hours ?) once per week or
so.  This is to desulfate the plates and get the sulfuric acid back in solution.  The more it sticks to the plates, the lower the SG will be able to get.

boB
Why would using End Amp not allow for Desulfating of the plates? 
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

Thanks for the Link Larry.  Good Read.   

What I have been trying to do with my SW charger, while not allowing the solar array to charge the batteries and not using any load (except the load that is draw for the inverter of about 38 Watts) ... I've been trying to establish a base line for charging and for comparing in the future.

Something I read in the Article you posted ....

Quote"The specific gravity decreases during the discharging of a battery to a value near that of pure water and it increases during a recharge. The battery is considered fully charged when specific gravity reaches its highest possible value."

And

Quote"To avoid erroneous readings, specific gravity measurements should only be taken after an equalizing charge and subsequent float charge for at least 72 hours. "

How does one determine the "highest possible Value" of SG?    Based on the next statement,  I guess I erroneously consider that value to be the point at which the batteries stopped rising in SG during an EQ charge.  Looks more like that value is set after an EQ and subsequent Float (the step I was leaving out)

I am trying to get an SG value on my hydrometer that represents a full charge of my batteries using my hydrometer realizing that my hydro may not be exact,  but at least if it is consistent,  it will be correct ... what ever that value is. 
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

ClassicCrazy

I don't think you are going to be able to accomplish what you want with the precision you are trying to get unless you had a whole bunch of batteries and tested and picked the ones  that were all balanced. That might not even exist. Like Bob said the inner and outer cells can vary because of temperature or other factors.

I guess I would go with the manufacturers SG and make sure you bring the lowest SG cells to that point and then don't worry about the ones that are higher SG readings you found. With a good absorb every ten days to mix up the electrolyte and equalization every month you are probably going to do the best you can . The only other option was to do it like Ross said in different post is to monitor each cell ( which you can't do with 6v batteries ) and balance the voltage on each cell like he said he does.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

boB

Quote from: Matrix on January 14, 2018, 01:41:27 PM
Quote from: boB on January 13, 2018, 11:49:56 PM

The way I understand it, EA shouldn't be used ALL the time...  i.e.  you will need to do a timed absorb (2 or 3 or 4 hours ?) once per week or
so.  This is to desulfate the plates and get the sulfuric acid back in solution.  The more it sticks to the plates, the lower the SG will be able to get.

boB
Why would using End Amp not allow for Desulfating of the plates?


Because  enough time may not have passed for the high voltage to do its job in that regard.  This would be because
if the batteries are always charged when the bulk/absorb cycle happens, the charge current will quickly fall below EA
instead of taking a long time.  This is what I have understood from the forklift and industrial battery folks.  This also
makes sense to me.

I think that what happens is that as the sulfation is allowed to sit on the plates, as it would do if NO absorb or EQ
were happening, then it tends to harden on the plates and will not easily return to the liquid between the plates.

When that happens, the SG will be lower than it was when the batteries were new because the electrolyte will
be more water than Hâ,,SOâ,,,   
One could add more acid to the mix and the SG should go up again but that won't fix the insulation on the plates
caused by the hardened sulfation.   Someone can adjust and correct my interpretation of all this but I think
that's it.   This would be a good one for Steve Higgins from Rolls batteries if he is on here.

boB
K7IQ 🌛  He/She/Me

Matrix

Thanks boB ... so if I'm using the Local App,  how do I turn EA off?    Do I ...
- Simply uncheck the WBJ box?
- or do I lower EA to Zero (0)?
- or some other method I have missed.

Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

boB

Quote from: Matrix on January 15, 2018, 02:03:19 PM
Thanks boB ... so if I'm using the Local App,  how do I turn EA off?    Do I ...
- Simply uncheck the WBJ box?
- or do I lower EA to Zero (0)?
- or some other method I have missed.

Just turn the EA to zero (0.0) amps

You want the WB Jr. on for state of charge

boB
K7IQ 🌛  He/She/Me

Vic

#14
Crap just lost a long post ...

Matrix asked "So am I correct.  The best way to control End Amps in the SW would be to change the Battery Capacity function? "

YES,  you are correct.

Deep Cycle batteries are designed to be CYCLED,   try cycling your bank  to 60,  or even 50% SOC  every few weeks or once per month.

Avoid charging your batteries when the measured SOC is above 90%.

Both of the above should help reduce the occurrence of SG readings above manufacturer's spec for 100% SOC.

OK on the Hydrovolt,  that should do well.

While charging your batts from the SW,   during Bulk,   measure the battery terminal voltage at the batteries,   where the inverter leads connect  --  measure on the terminals,  not the lugs of the cables.   Does this agree with what the SW's voltage?

YES,  battery manufacturers increase the electrolyte SG,   primarily to increase the Capacity of the battery.   A 15 point nominal increase will increase the Capacity by about 5% for FLAs.

AND,   have ALWAYS used EA to end Absorb on all systems here (even with CCs that used only the CC's internal Shunt).   This has always worked well.

We use WBjr EA,   in conjunction with Skip Days  on all of these systems,  as well.

However,  when choosing an EA value,  one must not just use the suggested value from the battery mfg.  Choose one that works for your system,   based on measured SGs,   and change the EA for your systems.

In addition,  the DOD of the battery in the previous cycle,   will affect the correct EA value  (YES,   this is a bit unfortunate).

If the Vabs is changed,   usually,   the EA value will need to be changed to match.

As FLA batts age,  generally,   the Vabs will need to be increased,   and the EA will also usually need to change,   as well.

AND,  battery monitoring devices are only as accurate as are the data entered into them by the user.   FLA batteries have a charge  Efficiency of about 85% when new.  This will decrease as the batteries age.

There are many variables involved  in trying to determine the SOC of a battery based on things that can be easily measured,  and potentially every battery bank may well behave differently in these factors based on just how it has been discharged,   and charged,   its age,   and so fourth.   Battery monitoring devices simply cannot know enough about the behavior of the bank,   based upon many of these variables,   so absolute accuracy suffers.

SO,   battery monitoring devices simply report approximations on SOC,   Remaining Capacity,    etc.   AND,   the larger the number of days since the last real full-charge,   the less accuracy they will have for the values reported.

If one is reading the battery monitor display,   and it says 67% SOC,   then it is probably best to think of this as,   approximately,  or about 60 or 70% SOC ...

Not to put too fine a point on it.   FWIW,  VIc
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!