advice needed for charging parameters exide jtt12v4800

Started by bennyspoon, October 22, 2018, 04:51:03 AM

Previous topic - Next topic

bennyspoon

Hey gang, I aquired some of these batteries at a decent price to use in my system.

I have contacted exide and they sent me one of the attached docs with no direct answers to my questions regarding charging regime. :(

It may be that they are not designed to be used in an off grid system,more for ups i think.

It seems to me that the float voltage is 2.27vpc and that the bulk charge up to 2.4vpc.

At 48v that would be 54.5 and 57.6, and i suppose absorb would be close to 55.

I will be using a whizbang jr and I am stuck trying to figure out the percentage change per degree c as stated in the doc as -0.005 x k.

Can anyone offer suggestions?

Cheers,
Ben.
48v system, 2 solar kids synced{1500w x2 arrays of trina honey 250w}with a 3rd kid synced for hydro f+p 700w turbine{early days!}, classic 150 for 4275w solar ,classic 250/ac clipper for wind {coming} , schneider xw+ 8548 inverter 645ah ex ups exide  jtt12v4800 ,3 strings{fingers crossed}.

alyaz

Fwiw, Rolls uses a formula that turns out affecting the final charging parameters depending on what your charging source is.  For example, my solar charging parameters are slightly different from my inverter charging parameters.  You could use their formula which may give you some numbers to help determine your parameters, based on other info you may have.  I know each battery is different, but just sayin... especially if you can’t get any thing firm from Exide.
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

Westbranch

Did they give a reference temperature? usually around 25*C
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

ClassicCrazy

#3
Quote from: Westbranch on October 22, 2018, 12:28:04 PM
Did they give a reference temperature? usually around 25*C

Yes on his attachment they have 25 deg C  and say it must be temp compensated ( though they don't say the temp compensation ) . They do have  temp compensation graph  so the milivolt per cell can probably be figured out from that .
Their info is kind of confusing on those graphs they have. I can't quite figure out what they are calling for charge times and voltage. It almost seems like they give the info for float charging at a C10 rate ?