PV Shade

Started by jtdiesel65, January 05, 2012, 03:34:27 PM

Previous topic - Next topic

jtdiesel65

Hi,

Can this be disabled? I was seeing this today with a little snow on the panels.  It was switching back and forth. The thing is output when "pv shade" was 0.5a, but I was seeing 4.5 with "bulk mppt".

thx

boB

Quote from: jtdiesel65 on January 05, 2012, 03:34:27 PM
Hi,

Can this be disabled? I was seeing this today with a little snow on the panels.  It was switching back and forth. The thing is output when "pv shade" was 0.5a, but I was seeing 4.5 with "bulk mppt".

thx

The newest software upgrade, which should be on our web site in just a few days from now, allows PV shade reporting
to be disabled.

boB


K7IQ 🌛  He/She/Me

mike90045

One thing I've noticed in the depths of the Morningstar MPPT settings, is a way to set or fix, the MPPT voltage to a fixed value, which may be useful for semi-obscured panels.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Halfcrazy

The Classic has this as well there is a couple modes that do this:

U Set VOC % this is where you program a percentage of VOC and it parks there. It will do timed sweeps to see if the VOC has changed and the time interval of these sweeps is adjustable.

Hydro mode has a VMPP voltage set point that you can program and it will park at that voltage and stay there.

The additions to Hydro Mode will be in the firmware release that should be available in about a week.
Changing the way wind turbines operate one smoke filled box at a time

laszlo


I am looking into some fuel cells that run on natural or bio gas, so it would be nice to able to explicitly  set the MPPT voltage and have it sit there and not do any sweeps.




Quote from: Halfcrazy on January 05, 2012, 09:53:49 PM
The Classic has this as well there is a couple modes that do this:

U Set VOC % this is where you program a percentage of VOC and it parks there. It will do timed sweeps to see if the VOC has changed and the time interval of these sweeps is adjustable.

Hydro mode has a VMPP voltage set point that you can program and it will park at that voltage and stay there.

The additions to Hydro Mode will be in the firmware release that should be available in about a week.
4.6KW offgrid PV system, Classic 200, MX60, dual Magnum PAE 4448 inverters, Midnite combiner and disconnect boxes, e-panel,  WBJr, and 8 MN SPDs