Question on wiring my SPD

Started by mickhill, May 18, 2019, 11:16:30 AM

Previous topic - Next topic

mickhill

Hey guys, new here. Just working on an off-grid solar project to run my small chest freezer and possibly fridge. I have 8 - 100 Watt Renogy panels going on the roof and right now, 4 - 125Ah Vmax AGM batteries run in parallel. The components will run down and feed into my utility room where the freezer is. I have a Midnite Classic 150 and a 2000 Watt pure sine inverter/charger. The combiner box Im using is an "Eco-Worthy" 6 string. Pic Attached. My plan is to wire a 115SPD at the combiner box but I guess I dont understand entirely how they work. It looks like it would "pass through" like a fuse but it seems to be wired in parallel. Does it just "eat" the surge? What stops it from going on through the wires to the inverter,etc ?

ClassicCrazy

system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

mickhill

Yeah, Ive watched no less than 20 videos from all over YouTube. Still not sure how it works but they all seem to be wired in parallel with the PV +/- in combiner boxes, so thats how I wired it. Just got it in the mail today. Hopefully it works if I ever need it to.

ClassicCrazy

When the voltage goes above a certain threshold - (surge or spike)  then the electronic components in the surge protector send ( clamp) the higher voltage to ground so it won't blast the protected devices on the circuit.

If you want the technical details this will help
https://www.electronics-tutorials.ws/resistor/varistor.html

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

boB

Right.  The MOVs in the SPD clamp or keep the voltage spike from exceeding a certain voltage.  Each SPD has two circuits of these with the GND being the common.

A device like the Classic has insulation between all its internal circuitry and ground, such as the chassis.  That insulation will break over when any of the connections coming into or out of the Classic (or whatever product that needs protecting) exceed some voltage.  Every Classic is tested to a high pot voltage.  The main four connections, battery plus, PV plus input and the two negatives are all tied together and treated to 2200 volts DC for one minute.
Other electronics products and even toasters will have this kind of test if it is listed to some NRTL like UL, ETL, TUV, CSA, etc.

So, the SPD is there to keep any of these connections from arcing over through that insulation to CHASSIS GND. 

Lightning is what is called a common mode voltage rise, meaning that both PV positive and negative rise together in reference to ground, which the chassis is tied to.   So, that's why the two SPD circuits are connected to PV minus and PV plus separately.  The SPD tried to keep those voltages from exceeding that 2200 volts.  It should actually keep it quite a bit lower than that but 2,200 V is the legal limit for the Classic.  So, for PV, the SPD 600 or even the SPD 300 should work fine.

Batteries are inside with shorter cables and not as much of an antenna for lightning so typically don't need protection.

boB





K7IQ 🌛  He/She/Me