Mnspd300vdc led on but mostly off

Started by mahendra, March 22, 2021, 11:14:54 PM

Previous topic - Next topic

mahendra

So I installed a Mnspd300vdc to an 12 array combiner and noticed that as the sun changes sometimes the spd led would sometime illuminate but mostly stays off. What can cause this my only guess is a floating ground. Any other thoughts?
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

mahendra

OK guys no need for a reply turns out it is a floating ground issue from a stripped screw thread in array panel. So issue solved when ground conductor from spd was placed on another available ground bus terminal.
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

KyleM

In hindsight that is so obvious .....   but that must have been a bear to find?