Fire sign on 12A breaker

Started by SolarMusher, July 05, 2012, 05:56:29 PM

Previous topic - Next topic

SolarMusher

Hi,
When changing my 4 years old PV combiner for an upgrade to a 300VDC combiner, after I removed the breakers block, I've seen sign of fire at the back of one 12A breaker (Solarworld 175W mono). This system was 48VPV/48VBatt with an MX60. I hadn't noted a lower Watts output before the upgrade. Everything was working fine. I wonder what could be the origin for this sign of fire (the combiner has also the same mark).
Thanks for your help,
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

mike90045

fire sign ?    you mean a stamped logo or soot and char marks ??
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

SolarMusher

Hi Mike,
I mean char mark on the Din Rail in the combiner, behind the breakers block and one breaker which has soot mark on its back (at the same place), but I have checked all my PV series and all seems to be fine.
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

boB


Whew !   I thought you meant   Firesign Theatre !!

(www.firesigntheatre.com)
K7IQ 🌛  He/She/Me

SolarMusher

Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

Halfcrazy

Erik
Any pictures? I can only assume it was arcing through to the din rail? I wonder if Ground Fault protection would have caught this? Or Arc Fault Protection. Maybe it was not arcing to the din rail but arcing internally?

Ryan
Changing the way wind turbines operate one smoke filled box at a time

SolarMusher

Hi Ryan,
I didn't have GFP installed on this old installation, because I wanted to upgrade to 72VDC with a Classic for summer. I think this breaker had to arc internally. But why only this one? It was on a Solarworld string of two 175W mono.
Two years ago, my whisper 200 was hit by a direct strike in the night, may be it could be one the reasons.
I would like to understand what was happened and if I made a mistake where I made it. Now that I know this could happen, I will check my combiner more often even if I think that my system is more secure with a Classic . This combiner is located on a log wall and I don't want this lodge to burn :) . I'll send you a picture.
Thanks Ryan,
Erik
Off Grid with 4kw PV | 2x Classic 200/WBjr | 2x Outback VFX3648 Epanel | 3x SPD300 + 1x Schneider HEPD80 | Hub + Mate + PSX-240 | Volthium 400Ah/51.2V LFP battery bank + Trimetric | 1500 watts AC water heater | Kubota 11kw GL diesel generator

Halfcrazy

I bet there is a connection between the lightning strike and this? It would appear from the description that there was an arc out to the din rail. I also suspect it was not continuous or the breaker would have eventually melted down.

Ryan
Changing the way wind turbines operate one smoke filled box at a time

niel


Robin

Good idea on the SPD. I wonder if moisture can be getting into the combiner and onto the breaker? It is normal to have some condensation in the combiner in the morning, but I have never heard of arcing? Lightning may have caused it, but at this point there is no way to tell. Make sure the combiner doesn't have holes in the top where the bends happen. If you can see air through the top, add silicone in the corners.
Robin Gudgel