Smart breaker sizing

Started by ASword, April 27, 2025, 07:44:09 PM

Previous topic - Next topic

ASword

The One has 3 smart breakers rated at 60/30/50.  These are designated for use as gen-in / smart load / AC coupled PV, respectively.

This is theoretically perfect for my situation as I have a generator, AC coupled PV, and a load I want to make smart.  The problem is that my gen is 8.5kW (say 40A), my AC coupled is 5.2kW (say 25A), and my wannabe smart load is 60A.

Is it possible to swap around the three smart breakers to be 50/60/30 instead of the original 60/30/50 setup?

ASword

Got an answer:  these things are hardcoded in the firmware.