WhizBangJr Installed

Started by Corndog, March 01, 2026, 12:02:15 PM

Previous topic - Next topic

Corndog

Hello,
I finally installed the Whizbang,
Can I ask -  it says (ON)(OFF). do I have this configured properly ? Copy and pasted from the Local App

AUX
AUX 1:  DIVERSION(Off)(Off)
AUX 2:  WHIZBANG JR(On)(Off)

Whizbang Jr.
System: 28.8A   Net Ah: 2Ah
Remaining Ah: 823Ah
SOC: 95%


Thank you
Our System
Off Grid
2 x Outback Flexware- VFX3648 Inverter
Mate 3
Power Hub 10
Hanwha solar panel 345 watts-- total array 5520 watts
Midnite CI150 Charge
13 KW Diesel Gen
48-volt System:
Sixteen x S6 L16-HC (445 AH) batteries, bank capacity of 890 AH @ 48-volts.

ClassicCrazy

The Whizbang uses Aux 2 so you should have the purple wire from the Whizbang on Aux 2 connection in the Classic. Then yes select Whizbang for Aux 2 . You should see a whizbang junior screen on the MNGP and there is a setup section on there. I think you can do all the same setup in the Local Status app too. It might take a day to go through the cycle to get all your new settings calibrated so the SOC starts working okay .
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

Corndog

Thank you , I was confused by the ON/OFF under aux 2 on the local app.  Was not sure if it should say ON/ON.
Our System
Off Grid
2 x Outback Flexware- VFX3648 Inverter
Mate 3
Power Hub 10
Hanwha solar panel 345 watts-- total array 5520 watts
Midnite CI150 Charge
13 KW Diesel Gen
48-volt System:
Sixteen x S6 L16-HC (445 AH) batteries, bank capacity of 890 AH @ 48-volts.