To visit MidNite Solar click this link www.midnitesolar.com
Quote from: Wirenut on March 10, 2026, 06:40:29 AMI realize the inverter will only do 30 amps. I was referring to the rest of the device: wiring, relays, etc. I think the AC output breaker in the Rosie breaker box is also a 60. Are you saying the Risie can use It's 30 amps of inverter capacity with 30 from the generatorfor 60 amps total to the loads? That would mean the breaker is good for 60 amps continuous?My apologies I made a mistake in previous post. Please ignore that.
Quote from: Wirenut on March 09, 2026, 10:01:27 PMDoes anyone know how much power can you get out of a Rosie inverter using generator support? Is it limited to the 60 amp output rating of the unit or something lower than that? I'm assuming the Rosie would make it's rated 7 kW and use generator power up to 7.4 kW to make the 60 amp output. Is this correct?When there's AC input it can take 30A of 240V (or 120V), to pass thru to loads and use any remaining current for its battery charger. The 60A inverter output rating is a 60 second surge value. Otherwise it would be 30A of 240V (30A on each 120V leg).
Thanks for your help.
Quote from: Corndog on March 02, 2026, 11:58:27 AMThank you , I was confused by the ON/OFF under aux 2 on the local app. Was not sure if it should say ON/ON.I just looked at Local Status app on my Classic and on the Config / Advanced menu the Aux 2 is set Whizgang Jr Auto