Quote from: Raster on May 21, 2025, 11:33:17 PMMahendra:

Is there a source for the trolley?

Thanks, R.

Sorry locally custom built.The pic show n is not the completed trolley I will post the updated one.

Once you have some fabrication skills it can be done take some time and effort though.
Dang I should have completed a CAD drawing.

I didn't relise it would have came out that good
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

mahendra

So another update guys,
One pack in the set of four power flow batteries gave a fault for serval times on Monday.
What was weirder is that every time it went to fault the entire system was shut off without warning or any code on mngp2 .
I was not pleased with either of these .
I tried getting help from tech support but they seemed Clueless as I was.
So I isolated the one alarming pack and found everything was fine beside this pack .
I operated in this manner for two days
So the only option was to check for firmware updates .
Only updates that were available were mngp2 and solar assistant ( I don't recall if I mentioned but system is now being monitored through solar assistant)
So far this seems to be the solving the issue but the whole system shutdown and no fault code reporting is getting me uneasy.
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

Brucey

Quote from: mahendra on July 19, 2025, 05:58:23 AMSo another update guys,
One pack in the set of four power flow batteries gave a fault for serval times on Monday.
What was weirder is that every time it went to fault the entire system was shut off without warning or any code on mngp2 .
I was not pleased with either of these .
I tried getting help from tech support but they seemed Clueless as I was.
So I isolated the one alarming pack and found everything was fine beside this pack .
I operated in this manner for two days
So the only option was to check for firmware updates .
Only updates that were available were mngp2 and solar assistant ( I don't recall if I mentioned but system is now being monitored through solar assistant)
So far this seems to be the solving the issue but the whole system shutdown and no fault code reporting is getting me uneasy.

Personally I would switch to open loop and run on voltage without any of the bms errors causing outages nonsense.

One reason someone had requested the ability to have battery comms to grab cell level data yet still run open loop based on voltage.

mahendra

Yea , unfortunately owner wants the bit of autonomy.
Had another brief shut down .
At this point I can't tell where it's coming from.
I am still suspecting the one power Flo battery.

Tech support has been really unhelpful. We were given another tech support number and  told to talk to Ron or Rick . They seem to be the powerflo guys.
Hope Midnite figure this out .
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

mahendra

Finally got the MP powerflo updated after several bms tools and software .
It would appears the one sent out by MNP is somewhat unique.

This seems to solve the battery issues so far.

I however had Rosie shutting off her output giving an alarm of over current and over temperature . Rosie has never been given a max load beyond 3000w and would normally have just around 500w .
So i have ruled put an actual over load

I did suspect a faulty ebike charger that usually charges and ebike.
But cant say why a tiny charger caused this.I got rid of the charger and the issue seems to have disappeared for now atleast.

Any thought or points on this are welcomed .
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

Brucey

Quote from: mahendra on December 02, 2025, 10:48:21 AMFinally got the MP powerflo updated after several bms tools and software .
It would appears the one sent out by MNP is somewhat unique.

This seems to solve the battery issues so far.

I however had Rosie shutting off her output giving an alarm of over current and over temperature . Rosie has never been given a max load beyond 3000w and would normally have just around 500w .
So i have ruled put an actual over load

I did suspect a faulty ebike charger that usually charges and ebike.
But cant say why a tiny charger caused this.I got rid of the charger and the issue seems to have disappeared for now atleast.

Any thought or points on this are welcomed .

Rosie could well have detected the crap charger and gone into protection. I used to have a horrible system of extension cords etc and at the end of one of those way down in the basement a fridge cord had become half unplugged and overheated. garbage Chinese breaker failed to trip, but Rosie eventually caught it, iirc it was an overcurrent fault. House went dark, investigated Rosie, saw the error, went downstairs smelled charred electrical, a light haze down there....

The Rosie engineers definitely know their stuff.

mahendra

Thanks, though the same .
Just checking my sanity   :D
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

mahendra

Some new errors from Rosie .
Had to shutdown.s
eems like powerflo battery no.2 again causing issues.

All updates are just before the recent 19 December 2025.

Will update and to most recent and check.

Rebooting didn't resolve.
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

ClassicCrazy

Quote from: mahendra on December 28, 2025, 01:55:18 PMSome new errors from Rosie .
Had to shutdown.s
eems like powerflo battery no.2 again causing issues.

All updates are just before the recent 19 December 2025.

Will update and to most recent and check.

Rebooting didn't resolve.

Why don't you just go to open loop charging ? Unplug the canbus cable and put in the Absorb, absorb time, and Float .  It works pretty good .
Larry
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP

mahendra

Will do that if it repeats.

I found the Midnite temp sensor was reporting incorrect battery temperature- 42-45 degrees celsius causing a low batt temp warning.
Tried unplugging, still the same

Swapped it out and resolved the issue so far.
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 wbjr ,180ah CALB Lifepo4 48v battery bank,jkbms 150amps bms(top balanced) Outback vfx3648.
Soon to be added Sol Ark 8k with 5Dyness Bx51000 ,7.8kw pv

UpNorthMan

Are you using the temp sensor/ comp with your batteries? If you are, I believe that lithium batteries don't use it and could potentially harm your batteries.
1000W panels Kid CC 230ah battery bank @48v
Weekend cabin, 250w inverter.
Waiting for the new inverter to be released so I can finish my install!

ClassicCrazy

Quote from: mahendra on December 29, 2025, 10:31:56 AMWill do that if it repeats.

I found the Midnite temp sensor was reporting incorrect battery temperature- 42-45 degrees celsius causing a low batt temp warning.
Tried unplugging, still the same

Swapped it out and resolved the issue so far.

You could ohm the temperature sensor and make sure it is the correct resistance. The should change as you heat or cool it off.
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal 24v pack , Outback 3524 inverter
 5s 135w Kyocero , 3s3p 270w Kyocera   Classic 150 ,8s2p  Kyocera 225w to Hawkes Bay Jakiper 48v 20kwh  ,Gobel 16 kwh  lifepo4 Outback VFX 3648  8s2p 380w Rec pv EG4 6000XP