Started by schroew, January 28, 2022, 08:18:31 PM

Previous topic - Next topic

schroew

I am getting an ecogen generator installed in a few weeks and would like to know if it is approved/supported to put a SPD AC on the AC line into my Magnum inverter ?

mike90045

I'd put one on the Gen input and also on the Grid input
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

schroew

No grid for me. Thx for the reply. I’ll pickup a couple this morning.

schroew

It was ordered last April and just arrived if anyone was wondering.

schroew

This works with 120v ac? I dont have any 240v breakers in my panel and the generator input is 120v..

boB

#5
Quote from: schroew on May 31, 2022, 10:13:59 PM
This works with 120v ac? I dont have any 240v breakers in my panel and the generator input is 120v..

Yes, an SPD-300 will work with 120VAC.   120V to GND and Neutral to GND with the two halves.

Oooops...   Bad wording. Fixed  😁
K7IQ 🌛  He/She/Me